Hi everyone!
I'm triying figure my cooling fan in the programmable outputs area but i can't find the correct form to this. I'm using the JS3, IAC2. With this setup my fan turns ON when the car start. I cant find a fan area to work with the ON temp and OFF temp. Thanks for the help!
MS2 Programmable Outputs
Moderators: jsmcortina, muythaibxr
-
- Site Admin
- Posts: 39618
- Joined: Mon May 03, 2004 1:34 am
- Location: Birmingham, UK
- Contact:
Re: MS2 Programmable Outputs
You have the output set to be on as soon as you power up the Megasquirt and turn off when the temperature is reached.
i.e. you have
"Power On Value" = "On"
"Active Value" = "Off"
I would suggest you want:
"Power On Value" = "Off"
"Active Value" = "On"
This is mentioned in the manual : http://www.msextra.com/doc/pdf/html/Meg ... 3-146.html
James
i.e. you have
"Power On Value" = "On"
"Active Value" = "Off"
I would suggest you want:
"Power On Value" = "Off"
"Active Value" = "On"
This is mentioned in the manual : http://www.msextra.com/doc/pdf/html/Meg ... 3-146.html
James
I can repair or upgrade Megasquirts in UK. http://www.jamesmurrayengineering.co.uk
My Success story: http://www.msextra.com/forums/viewtopic ... 04&t=34277
MSEXTRA documentation at: http://www.msextra.com/doc/index.html
New users, please read the "Forum Help Page".
My Success story: http://www.msextra.com/forums/viewtopic ... 04&t=34277
MSEXTRA documentation at: http://www.msextra.com/doc/index.html
New users, please read the "Forum Help Page".
Re: MS2 Programmable Outputs
If i change values the fan turns ON all the time. The only form to maintain the fan OFF when i open the power switch is with a 20.0 of hysteresis, and "Power On Value" = "On" / "Active Value" = "Off". I dont know what cause this. Thanks!
-
- Site Admin
- Posts: 39618
- Joined: Mon May 03, 2004 1:34 am
- Location: Birmingham, UK
- Contact:
Re: MS2 Programmable Outputs
The on/off thing is because you've wired up the wrong "half" of IAC2. It will work as you have it wired and set though.
James
James
I can repair or upgrade Megasquirts in UK. http://www.jamesmurrayengineering.co.uk
My Success story: http://www.msextra.com/forums/viewtopic ... 04&t=34277
MSEXTRA documentation at: http://www.msextra.com/doc/index.html
New users, please read the "Forum Help Page".
My Success story: http://www.msextra.com/forums/viewtopic ... 04&t=34277
MSEXTRA documentation at: http://www.msextra.com/doc/index.html
New users, please read the "Forum Help Page".
Re: MS2 Programmable Outputs
Thanks James! Can you help me with the wire up?
Re: MS2 Programmable Outputs
When ProgOut 'IAC2' is ON, pin IAC2A is at +12v while IAC2B is at GND. When IAC2 is OFF, IAC2A is at GND while IAC2B is at +12v. Like James said, you can leave it alone and revise your settings appropriately, OR, you can move your wire to JS2 and have more straightforward settings.
Temporarily shut down - back soon!
QuadraMAP Sensor Module -- PWM-to-Stepper Controller -- Dual Coil Driver
Coming soon: OctoMAP Sensor Module
TTR Ignition Systems
QuadraMAP Sensor Module -- PWM-to-Stepper Controller -- Dual Coil Driver
Coming soon: OctoMAP Sensor Module
TTR Ignition Systems